Harmonic issues in residencies, I find that very hard to believe.
To answer your question about wiring.
In my street there is a local distribution transformer - it is about a 1500 kVA, 11kV to 400/230V with a delta primary and star (Y) secondary. The The houses are fed with the single phase line to neutral 230V and loading is distributed around the phases.
So, low voltage single phase derived from a higher voltage three-phase supply. I perhaps ought to add that there is no heavy industry anywhere near us.
We are quite close to our local transformer so the voltage we get is probably not greatly dissimilar to that at the transformer terminals.
And it contains quite a high proportion (about 4%) of third harmonic distortion. That much is immediately evident from the flattened top in the waveform. There was a bit of seventh and a spread of the other usual suspects. This taken today at around 5:30 pm local time.
Does it cause me problems?
I can't say for sure that it does. I've had a couple of conventional ballasts fail in the same fitting the past year. It's the only conventional ballast we have. One of the lights in our hallway has failed just a bit more often than I would have expected. It could all be coincidence of course. If this pattern is replicated in a number of houses fed from that same supply then it just might be stretching that coincidence. I don't know whether it has - as a rule, failure of ballasts and quality of supply isn't something that comes up in casual conversation with the neighbours.:grin:
But one thing about which there is no doubt is that our supply has significant harmonic distortion the cause of which exactly fits with the proliferation of single-phase non-linear loads.
I'm pretty sure there is similar distortion on some or many other supplies in residential locations. In fact, at the pumping station I mentioned a few posts back, the average over a 24-hour monitoring period was 3.67% and for the 10pm to midnight slot it was 4.15%.