surf more
- eastern NC
i came across a service for a duplex,and it seemed wrong.
it was a 3 gang meter can,one meter for each ,with middle blanked (power company)
#1
from one meter they took 2=2/0-1=1/0 from meter to 8-16 200amp hom mainbreaker meterpanel combo which was under meter bank.the installer put another breaker in to feed subpanel inside.
#2
from the other meter (200amp meters) they fed #4 down below meter bank to a 100amp hom disconnect to the main lugs,and then installed a 100amp breaker to fed subpanel.
#1 was correct
#2 correct?me!!I would think the way i read 230 that it would be fine if wiring from meter went to 100amp breaker first as long as it was secured(breaker),and then the wire from sub panel went to main lugs!
is it legal to run straight to mainlugs from meter ,if that is the only breaker in that panel?i see 6 motions of hand ,but i think#2 was wrong,but that is why i am posting so correct me please if i am wrong!!
i was thinking that if you wired from meter to a main breaker that would be service disconnect,because the way it was wired the buss would still be hot wired to main lugs.
the #4 from 200amp meter to 100amp disconnect??i did not think that was correct either!!
i was on a service call ,and noticed!!it got me thinking
#1
#2
#1 was correct