I have been reading this thread:
http://forums.mikeholt.com/showthread.php?t=115549
and it has answered a lot of questions, but I have a LENZE
motor that this nameplate data:
LENZE A-4470 Enns Austria
DS100L/4 B9 55 IP
3.6 kw | S1 |lz F
50 HZ | 1400 RPM
wye/delta 220-240 /380-415 Volts
12.6/7.3 Amp | cos 0.81
60 HZ | 1680 RPM
wye/delta 220-266 / 380-460 Volts
12.6/7.3 Amp | cos 0.85
No. 508887 | 1995/50
I connected a siemens G120 VFD to it, tuned it using the
60 hz 460 volt settings, but the motor was wired in the
wye method. It ran ok, but could stall easily, and only
supplied an output of 3.7 amps max before stalling.
So, I rewired the motor to delta, thinking this would fix
the torque issue. The dive could not complete the auto-
tune, it could not even do a standstill saturation tune.
The motor would only oscillate back and forth, and I had a
Siemens drive guy helping me!
To get it running well enough, we had to wire the motor connections
back to the wye configuration, and use the 12.6 max amp
ratings for the drive current parameter (which I thought would
only apply if the motor was using 230 volt supply).
My question is why did the drive have so much trouble
when this six lead motor was wired for delta, and do the dual
voltage ratings on the motor nameplate mean that 230 or 460
volts can be applied to both wye and delta configurations, or
does each wiring method need a specific voltage?
Sorry for long topic, but it was a long night, and I am
trying to learn about getting this done correctly. Thanks.
http://forums.mikeholt.com/showthread.php?t=115549
and it has answered a lot of questions, but I have a LENZE
motor that this nameplate data:
LENZE A-4470 Enns Austria
DS100L/4 B9 55 IP
3.6 kw | S1 |lz F
50 HZ | 1400 RPM
wye/delta 220-240 /380-415 Volts
12.6/7.3 Amp | cos 0.81
60 HZ | 1680 RPM
wye/delta 220-266 / 380-460 Volts
12.6/7.3 Amp | cos 0.85
No. 508887 | 1995/50
I connected a siemens G120 VFD to it, tuned it using the
60 hz 460 volt settings, but the motor was wired in the
wye method. It ran ok, but could stall easily, and only
supplied an output of 3.7 amps max before stalling.
So, I rewired the motor to delta, thinking this would fix
the torque issue. The dive could not complete the auto-
tune, it could not even do a standstill saturation tune.
The motor would only oscillate back and forth, and I had a
Siemens drive guy helping me!
To get it running well enough, we had to wire the motor connections
back to the wye configuration, and use the 12.6 max amp
ratings for the drive current parameter (which I thought would
only apply if the motor was using 230 volt supply).
My question is why did the drive have so much trouble
when this six lead motor was wired for delta, and do the dual
voltage ratings on the motor nameplate mean that 230 or 460
volts can be applied to both wye and delta configurations, or
does each wiring method need a specific voltage?
Sorry for long topic, but it was a long night, and I am
trying to learn about getting this done correctly. Thanks.