ncor

Member
#250 for a service entrance run to a 200A panel 388' from meter
or will a triplex 4/0 suffice over that distance
thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
#250 for a service entrance run to a 200A panel 388' from meter
or will a triplex 4/0 suffice over that distance
thanks

I assume you mean aluminum. To figure VD you really need to know what the load is. If you want a 200 amp load then 500KCM aluminum is what you would use to avoid 3% VD if that's what you want to do.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The NEC does not require you to upsize for VD in this situation. It would be a design issue. 388 feet is a very long distance and to have a 3% drop with just a 100 amp load you need 250KCM. Personally I would go with the 500KCM because you are going to be the one they call the first time the lights dim. :)
 