I am trying to size a breaker and cables from an MCC feeder breaker to feed an VFD.
When sizing a breaker for a VFD I believe the code says that the cables must be rated at 125% of VFD input current. I would assume then that the feeder breaker would have to be at least 125% as well? Or would you want to size the breaker up to the capacity of the cables?
Does it matter if the cables and breakers are rated above 125%? Is there a limit to how high these ratings can be over drive input current?
I know the drive protects itself from overload, but will it protect itself from short circuits as well?
If there is already a feeder breaker feeing the drive is it necessary to have a breaker at the drive itself other then preference? Would the breaker at the drive be redundant?
If using two breakers should the one at the MCC be larger than the one at tht drive itself?
When sizing a breaker for a VFD I believe the code says that the cables must be rated at 125% of VFD input current. I would assume then that the feeder breaker would have to be at least 125% as well? Or would you want to size the breaker up to the capacity of the cables?
Does it matter if the cables and breakers are rated above 125%? Is there a limit to how high these ratings can be over drive input current?
I know the drive protects itself from overload, but will it protect itself from short circuits as well?
If there is already a feeder breaker feeing the drive is it necessary to have a breaker at the drive itself other then preference? Would the breaker at the drive be redundant?
If using two breakers should the one at the MCC be larger than the one at tht drive itself?