Hope this reply is not too late...
Hope this reply is not too late...
My day job is with a POCO and I spend most of my time specifying underground (UG) equipment for the Distribution system.
RCWILSON did a good job of explaining the positioning of the Load Break Elbows and the Lighting Arresters in padmounted transformers. I will be attaching a few pictures of a three phase padmount with LA's, a single phase with LA's, a two way feed through bushing which plugs the elbow LA and the UG cable into it, the elbow LA by itself, and then a cut out of the LA that shows the arc follower rod that extinguishes the arc when pulled out of the bushing and then the MOV disks.
I do have to respectfully disagree with Mr. Wilson though on one item, lighting LOVES UG cable. That is the main reason utilities install LA's at normal open point transformers in an UG loop and on riser poles where the overhead turns to UG. There is a difference between direct lighting strikes and induced lighting strikes. The UG distribution system is very susceptible to induced lighting strikes. Lighting hits the ground and can find the UG cable and then hop on the cable looking for an even lower impedance ground path.
The loop UG system provides increased reliability to the customer. A lot of utilities claim that an overhead radial distribution system is the reliabilty equivalent to a looped UG distribution system. This is because the radial overhead and the looped UG will have similar restoration times.
Varczar, P.E.