augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
lots of "depends" :)
25 kw @ 208 3 phase evenly distributed would be 69.4 amps

422.10 would require an ampacity of 86.8 amps in most cases

From there, it's a case of type wire, etc. #3 THHN normal conditions, yes
#3 NM, no #3 SE Interior wiring '05 Code yes '08 Code no
 

Duffin

Member
I do not know what that means. All I have is the information I stated, 25kw
at 69.39A. Says #3 wire is needed and would like to know how they came up with the wire size. What size breaker would you use?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What type of equipment are we dealing with ? (air handler with unit heat, duct heater, heat pump, package air unit, water heater)
 