20 amp3 phase breaker.

Status
Not open for further replies.
so far i havnt been able to locate an exception for "not" doing this. Is it safe to use a 3 phase breaker for a 220/20 amp outlet - (a/b phase). and also use the c phase on the same breaker for the 120v 20 amp outlet? both circuits with a dedicated neutral.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

I have moved this post to it's own thead so it doesn't hyjack the original thread as well as providing more views.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Seems fine to me as long as you don't mind both loads going off at the same time for maintenance or if one trips.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I agree with Rob. Not a good design, because of maintenance constraints, but not unsafe, and not a code violation.

Welcome to the forum.
 

jwjrw

Senior Member
could an inspector claim 110 due to the common use for a 3pole breaker is for a 3pole equipment?
 
Status
Not open for further replies.
Top