What is the effect called if just a hot conductor is run by itself in a conduit?

By running a neutral or a ground it will cancel out this effect?

:roll:
Trying to remember this... At one time I knew. Thanks
 

broadgage

Senior Member
Location
London, England
Often called induction, even though some say that this is not strictly correct.

Running only the hot conductor in a steel conduit will cause excesive voltage drop, with the "lost" energy appearing as heat.
Adding a ground wont help since the ground/EGC is purely a safety feature and normaly carries virtualy no current.

What is required is to add one or more other current carrying conductors, such that the currents "cancel out" and dont induce currents in the conduit.

On a 2 wire 120 volt circuit, hot and neutral should be run together.

On a 2 wire 240 volt circuit, the 2 hot conductors should be run together, no neutral is needed to avoid induction effects. If however the load requires a neutral for proper operation, then this must be run in the same conduit as the hots.

The two wires to a light switch should run in the same conduit, both are hot, not neutral, but are in oposite directions and therefore cancel out.

If plastic conduit is used, then no heating will be caused, but the same rules should still be followed, since electromagnetic fields will be radiated by unbalanced currents, and some believe this to be dangerous to health.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
By running a neutral or a ground it will cancel out this effect?
As suggested by the previous responses, it's not necessarily the neutral conductor, but any circuit or feeder conductors. Basically, the same rules as GFCI's require.

All currents for a given load/circuit should be grouped, so the net total is zero. Any current in one direction is matched by the same current in the opposite direction.
 

domnic

Senior Member
Occupation
Electrical Contractor
Induction

Induction

The two wires to a light switch should run in the conduit. but are in opposite directions and therefore cancel out. Can please you explain this.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes. The wires of a two-wire switch loop have opposing currents exactly like the two sires supplying a load.

Picture a ceiling-fixture box with an incoming hot and neutral, and a 2-wire cable to a switch:

The fixture currents in the two switch loop conductors are identical to, including opposing each other, to the currents that the two supplying conductors carry.
 

Smart $

Esteemed Member
Location
Ohio
Addendum: Stated more correctly, it would be "The cause being alternating induction..."

If the one wire of the circuit were powered by DC voltage, there would be no heating.
 