I have an application that will use a single motor that is rated for continuous duty but will be run intermittingly. Should the conductors be sized per NEC Article 430.22 (A), motor FLA X 125% or use NEC Table 430.22(E) Duty Cycle Service, that states that a continuous rated motor for intermittent duty the conductors shall be sized at motor FLA X 140%?