In my normal electro hydraulic work, I am able to use current to accomplish all that is required; the customer is interested in not overloading the motor "much".
I've been asked to look at 4 motors (50 hp, 480-3-60) simultaneously and record (I have the data acquisition equipment) the power consumption (kW) vs machine cycle (obtained by pressure transducer). He's after something better than a linear approximation between no load and full load current; that has worked for me in the past.
This will be a rather short test (perhaps 2-4 hours), and we MAY want to look at 4 different motors after initial work.
My issues are:
I know of no way to make the potential connection and leave it for the several hours that is compliant with 70E.
I cannot shut the system down to install CTs, but there is access to insulated motor conductors, so they must be either split core or clamp on. I suppose that we could pre-identify the loads and have CTs installed during a scheduled shutdown. 6 or 8 years back, I saw a unit by Hioki which met the needs, but 4 of their their present 3169-21 and the 12 CTs is a little overkill for this one-time need.
Have any of you done something like this before, and do you have any suggestions?
Thanks!
George
I've been asked to look at 4 motors (50 hp, 480-3-60) simultaneously and record (I have the data acquisition equipment) the power consumption (kW) vs machine cycle (obtained by pressure transducer). He's after something better than a linear approximation between no load and full load current; that has worked for me in the past.
This will be a rather short test (perhaps 2-4 hours), and we MAY want to look at 4 different motors after initial work.
My issues are:
I know of no way to make the potential connection and leave it for the several hours that is compliant with 70E.
I cannot shut the system down to install CTs, but there is access to insulated motor conductors, so they must be either split core or clamp on. I suppose that we could pre-identify the loads and have CTs installed during a scheduled shutdown. 6 or 8 years back, I saw a unit by Hioki which met the needs, but 4 of their their present 3169-21 and the 12 CTs is a little overkill for this one-time need.
Have any of you done something like this before, and do you have any suggestions?
Thanks!