Field Assembled extension Cords.

Status
Not open for further replies.

eric9822

Senior Member
Location
Camarillo, CA
Occupation
Electrical and Instrumentation Tech
The way I read it:

Field assembled extensions cords can be supplied by a branch circuit that has a maximum 20 amp OCPD if the conductors are 16AWG or larger. Nothing says the the circuits OCPD cannot be lower.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Here is the NECHB commentary following 240.5(B)(4).

Field-assembled extension cords are permitted, provided the conductors are 16 AWG or larger and the overcurrent protection for the branch circuit to which the cord is connected does not exceed 20 amperes. The cord and the cord caps and connectors used for this type of assembly are required to be listed.
Is this a 590 install?
 
Not so fast :D. Section 240.5 tells us to use either (A) OR (B) to determine OCP for an extension cord. Section (A) tells us that we need to use tables 400.5(A/B). Under specific circumstances section (B) allows smaller gauges to be used that the 400 tables would allow, and (B)(4) allows the use 16g and 14g on a 20a OCPD for a field assembled cord set.

So I can field assemble a 200a extension cord set provided that all of the components are rated for 200a and the usage.
 
Excellent and Thanks much. Does the usage of cord for extension cords meet the uses permitted by 400.7?
 
Last edited: