Siemens or Square D 400amp Main Disconnect?

Status
Not open for further replies.

powerplay

Senior Member
I was curious if there are issues with having an 400amp single phase Siemens Main Disconnect, split to feed a 200Amp Square D panel and a 125Amp Square D panel in a restaurant. The Siemens is 5.5 inches more narrow with the handle infront saving at least 6 inches off the wall I am mounting to, but am I compromising quality?? Like Coke n Pepsi...what's the difference???? The service is coming in on overhead parallel ACWU cables as requested. Thanks again in advance for the excellent feedback!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Other than making sure you stay within tap rules, and using double lugs, there's no issue.

As for brand, if space is at a premium, go with the narrower one. Otherwise, go by price.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
There are design differences in those two specific brands. I would go with the Siemens, it uses double-break contacts as opposed to a hinged switch in the Sq. D. The hinged switch tends to be extra susceptible to corrosion over time.

Full disclosure; I used to work for Siemens but they no longer pay me to care :roll:, but this is my engineer head speaking.
 

wireguru

Senior Member
Are series ratings going to be an issue? 400 amp commercial service might have higher than 10ka fault current available....
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Are series ratings going to be an issue? 400 amp commercial service might have higher than 10ka fault current available....
No.

UL listed series ratings using fuses are not manufacturer dependent, unlike with breakers.

And if they were, it would be the fuse not the switch that would matter.
 

wireguru

Senior Member
No.

UL listed series ratings using fuses are not manufacturer dependent, unlike with breakers.

And if they were, it would be the fuse not the switch that would matter.


I didnt see the word fuse which led me to believe it was an enclosed circuit breaker... thanks for clearing it up.
 

mull982

Senior Member
Other than making sure you stay within tap rules, and using double lugs, there's no issue.


For this would you designate one secondary feeder the primary feeder and therefore designate the other one as a tap feeder? Or would they both be considered tapped due to the arrangement?

When you say "double lugs" I assume you are referring to using seperate lugs for each circuit. Is this a code requirement?
 

kwired

Electron manager
Location
NE Nebraska
For this would you designate one secondary feeder the primary feeder and therefore designate the other one as a tap feeder? Or would they both be considered tapped due to the arrangement?

When you say "double lugs" I assume you are referring to using seperate lugs for each circuit. Is this a code requirement?


They are both taps unless a 400 amp conductor is brought to each of the smaller OCPD's then they are feeders.

double lugs are need unless using a lug designed for 2 conductors.
 