I am not so interested in sizing the branch circuit. The nameplate data says 40A, that's how I'll spec it.
I'm more interested in sizing the panel load and the service load. In this case these are being installed into a new apartment building, approximately 50 total apartment units. The service is 208V/3P/4W to the building, 208V/1P/3W to each dwelling unit. I am using Part IV optional feeder and service load calculations.
For the individual dwelling unit panel 220.82 applies. Paragraph (A) states this section can be used to calculate feeder and service loads in-lieu-of Part III. Skip to (B)(3), the range nameplate data should be added in full and then if applicable can be derated at 40% (per paragraph 220.82(B)). So assuming the information on the following link is correct, I should use 7.9 kVA at 208V.
http://products.geappliances.com/ApplProducts/Dispatcher?REQUEST=SpecPage&Sku=JB680SPSS
For the service panel (meter stack) which feeds all the units 220.84 applies. All parts of (A) are met. Skip to (C)(3), the range nameplate data should be entered in full and then the appropriate derating factor can be applied per Table 220.84.
So in both cases I am not using Table 220.55, as that is in part III and I am in Part IV optional which excludes this table. I must use the nameplate rating, and cannot take 80% of 40A as I had originally assumed.
I'm pretty sure that is the correct procedure, but let me know if you see something fishy.
(Thanks JAMAN for catching the conflicting information on the manufacturer's website. I'll use the 7.9kVA value as it intuitively makes more sense.)