Is this a violation???

Status
Not open for further replies.

DownRiverGUy

Member
Location
Canton, MI
Ok so ignoring the workmanship issues and any issues with supporting the conduits that feed this monster.... would you consider this a violation? :D

If so please cite what section.

While I would die a little inside if I saw this I am not sure if it is a code violation... just a great example of wasting a lot more time/material doing something the wrong way.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Job specification: Provide a NEMA 1 junction box with 96, 3/4" knockouts.

Contractor: No problem. I've got it covered.

:)

Steve
 

iwire

Moderator
Staff member
Location
Massachusetts
That is an old picture that has been floating around.

If all the boxes where facing the right direction I would say no NEC violation.
 
314.22 surface extensions - wiring method shall be flexible for a lenth sufficient to permit removal, to provide acdcess to the box.

300.15 (A) covers shall be accessible after installation.

312.5 (A) openings to be closed - conduit connector in bottom box

314.25 each box shall have a cover

314.28 (C) covers compatible with the box

314.72 (E) suitable box cover and readily accessable

410.22 outlet boxes to be provided with a cover


Some where I rember being told that piping from an extension ring is not allolwed. It may be a local thing. So then what about the box which allows attachment to a one gang opoening?
 

iwire

Moderator
Staff member
Location
Massachusetts
314.22 surface extensions - wiring method shall be flexible for a lenth sufficient to permit removal, to provide acdcess to the box.

Agree

300.15 (A) covers shall be accessible after installation.

Agree

312.5 (A) openings to be closed - conduit connector in bottom box

Agree


314.25 each box shall have a cover

Kind of a stretch in my opinion, all places for covers are closed.

314.28 (C) covers compatible with the box

Kind of a stretch in my opinion, all places for covers are closed.

314.72 (E) suitable box cover and readily accessable

Not unless those boxes contain conductors over 600 volts .... and I think we all hope they do not.

410.22 outlet boxes to be provided with a cover

Applies only to lighting outlets, see 410.1


Some where I rember being told that piping from an extension ring is not allolwed. It may be a local thing.

I think it is just a myth.


So then what about the box which allows attachment to a one gang opoening?

Not following you.
 

WDeanN

Member
The picture is upside down. Flip it over, you can see the to of the sheet rock wall.

I see what looks like emt running across the top of a wall, but I don't believe that they are using wooden joists to support a metal beam... , or that those other wires are held up with spring tension...
 