I'm doing a 7 story time share. I found penetration details for PVC and EMT conduit. I can't seem to fing MC cable firestop details for thru floor (concrete) or Block walls. Anyone know if Hilti has details for these?
Haven't heard back from my Sales Rep.
 

ohmhead

Senior Member
Location
ORLANDO FLA
I'm doing a 7 story time share. I found penetration details for PVC and EMT conduit. I can't seem to fing MC cable firestop details for thru floor (concrete) or Block walls. Anyone know if Hilti has details for these?
Haven't heard back from my Sales Rep.

Well scottam Here in orlando when we run MC thur wall or floor we use a metal sleeve fill it with fire stop . The sleeve is poured in place during deck pour

Hilti makes a ready made sleeve your push your conduit up from the bottom and your done but its not for MC .
 