love9099
Member
- Location
- Salt Lake City
We have ran into several issues with Fire Alarm Cable when it comes to AHJs, Electrical Contractors and Specifications. Some of the Specs require THHN for fire alarm. I don't know if the Engineers don't understand that Non-Power Limited Fire Alarm Circuits are High voltage and that Power Limited are low voltage or not. Is this correct? NEC (NFPA 70) states that for POWER LIMITED fire alarm circuits that FPL, FPLR, FPLP and CMP wire is approved. We have some Contractors that install THHN for all their fire alarm, I understand that THHN is rated at 600 V and should exceed the requirements for fire alarm although THHN is listed for NON-POWER LIMITED in NEC it does not say you can use it for Power Limited. Am I missing some specific code reference? We have had fire marshals that have had issues with this. Normally I don't mind if an Electrical Contractor run THHN and the AHJ is ok with it. What concerns us more is when they install THHN when we clearly recommended FPL 18g/2c for an addressable loop in order to have the correct twists for data transfer. I understand all of us should install the correct cable to meet both the code and the manufactures recommendations. We had an AHJ make the Contractor pull out THHN that they ran for Horn/strobes because he said he wanted FPL and it was in conduit. I thought this was a bit much. Please let me know how you deal with these issues. I try to make it clear to the contractors the manufactures recommendations along with the code reference up front.