MDECONTRACTOR
Member
Called to site on intermittent tripping of 175A OCP on mulch coloring machine; MDP is adjacent with 300A main and several ancillary loads other than the 175A feed for the entire machine. Problem described as an "instant trip, like a dead short" only occasionally and with no apparent rhyme or reason. Observation of equipment and several motor starts were flawless; could not repeat fault condition while onsite. The 175A feed runs several things on the machine: VFD for small compressor; conveyor motor; water pump; auger motor. The only time the 175A OCP trips is when the main motor is started...and very infrequently at that. I thought perhaps there was a mechanical issue causing locked rotor, but you would think it would not cause immediate facilitation of the OCP and perhaps the overloads to trip; furthermore, there would be some obvious mechanical noise associated with this "binding" of which the operator did not speak. As well, there is a motor starter that is not tripping at any time. Now, the nameplate data is a 75Hp motor @ 480V which 430-250 indicates is 96 FLA and could have a higher rated OCP for starting; however, this equipment worked all last year with the same OCP and no problems. Now, this is my question to all you tech minded folks: Does this sound like an internal motor issue? Perhaps a faulty armature? I took phase current readings and all were balanced and within normal range. I am not certain if a 3 phase AC motor would or could have the same consequence of a simple dc starter motor on a car having a bad armature and not being able to turn until past that spot. Sorry for the ignorance here, just looking for some thoughts and throwing out some insight.