Is it legal to run the line and load conductors of a meter socket in the same raceway?
No. See 230.7 for related requirements.
I bet George was thinking meter main. or he is drunk:grin:
I bet George was thinking meter main. or he is drunk:grin:
Everybody run your answers by Bob first for his approval.
Is it legal to run the line and load conductors of a meter socket in the same raceway?
But if this is a service, the utility won't allow it.
Thanks for all the feedback, I really couldn't find the answer in the code. Here's the issue, I have a spare 4" PVC from the poco transformer to the CT cabinet and a spare 4" PVC from the CT cabinet to the inside of the building. I have to add a new 200 amp service, so I had a thought that I could transition the 2 conduits to a pull box then run 1 conduit to the new metersocket. Any thoughts?(This job is one of those think outside the box but keep it legal jobs)
Why wouldn't they and are you speaking for all utilities?
Roger
Yes. But if this is a service, the utility won't allow it, and you would need to derate the conductors.