I am getting similar voltage readings with my generator and I don't think the Sears genny you worked with is bad. Either that, or both generators need work
The other day at Costco I saw a genny with 'floating neutral' on the box. Research on this forum and web led me to check and see if I might have a bonded neutral in my backup (Generac 5.5kw) genny. I checked the owners manual, and sure enough, neutral was bonded to ground.
So I opened up the genny and found a jumper between the ground screw on one of the Nema 5 recepts and the neutral.
Here are the voltage readings I received before and after removing the jumper:
Before:
Nema 14 recept.: A-B 269; A-N 134; A-G 134; B-N 135; B-G 133
Nema 5 recept, A phase: A-N 136; A-G 135
Nema 5 recept, B phase: B-N 136; B-G 135.
Ideal plug tester in Nema 5 recept. showed two lights, normal.
After removing the jumper:
Nema 14 recept.: A-B 271; A-N 136; A-G 62; B-N 136; B-G 71
Nema 5 recept, A phase: A-N 135; A-G 62
Nema 5 recept, B phase: B-N 133; B-G 72.
Ideal plug tester in Nema 5 recept. showed one lights, open ground.
We have normal voltage a little above 120/240 where I live. I've used the genny (via a 100 amp CH transfer switch) on two occassions for a couple hours each with no problem.
Regarding the hot-ground readings, it looks like the frame of the genny isn't a very good earthing source, and that is why we should use GFI protection on our circuits at construction sites.
My web research came up with the nugget that OSHA requres the generators on work sites to have a ground-neutral bond. I didn't confirm that with any official site, however for temporary power I belive that the G-N bond at the genny should be removed to comply with NEC as a non-sds system. Your Sears generator likely didn't have the bond or you would have gotten a full reading on your hot-ground check.
I found this web site to be informative:
http://members.rennlist.org/warren/generator.html
Hope this information is of use to you.