I need to replace some wiring that was burnt due to a fault and over fusing and I had a couple of questions on how to arrrive at the wire size.
The motor is 440v 3phase 40hp. Its FLA is 52A. It is in an envoronment that can get as hot as 125 degrees. so I was going to use THHW or THHN.
First do I have to make the wire capability 125% of the load it is a continuosly running motor? that would make the amperage 65A?
I also thought for temperature I would have to derate the wires ampacity by multiplying it by .76 for a correction factor?
Here is where it gets even trickier the wire runns in conduit for about 70ft with 5 wires total, 3 for the 440v and 2 for control power 120v for a door switch. Would this be considered 5 current carrying conductors cut it down to 80%?
Tricky part 2 the last 30 ft runs in an open cable tray ( grated with large circular holes) to a motor control center with many wires in it would I have to derate for that?
Finally how would I fuse it. Thanks for the refresher course!!!!!
Dave
The motor is 440v 3phase 40hp. Its FLA is 52A. It is in an envoronment that can get as hot as 125 degrees. so I was going to use THHW or THHN.
First do I have to make the wire capability 125% of the load it is a continuosly running motor? that would make the amperage 65A?
I also thought for temperature I would have to derate the wires ampacity by multiplying it by .76 for a correction factor?
Here is where it gets even trickier the wire runns in conduit for about 70ft with 5 wires total, 3 for the 440v and 2 for control power 120v for a door switch. Would this be considered 5 current carrying conductors cut it down to 80%?
Tricky part 2 the last 30 ft runs in an open cable tray ( grated with large circular holes) to a motor control center with many wires in it would I have to derate for that?
Finally how would I fuse it. Thanks for the refresher course!!!!!