I have had a study done on a distribution system including:
-Arc Flash
-Coordination
-AIC
There are a number of breaker panels with a much higher available fault current than the the AIC of the breakers.
My question is in the difference between the 1,2, & 3 pole breakers.
For example: If a panel has an available fault current of 26,000A @ 480V 3-ph, do I need to size the single pole breakers that high as well as the 3-p? Or can I reduce the amount of AIC needed for the 1-P breakers?
The engineer that did the study said that the AIC needed to be the same whether 1,2 or 3 pole. But it seems to me that the fault current on one leg would be significantly less than a 3-ph bolted fault.
Thanks,
If more info is needed, let me know.