RETRAINDAILY
- PHX, arizona
What are the benefits to a VFD besides speed control ?
controlled acceleration and deceleration, ability of controller to interface with other electronics for many reasons.
Energy saving if you can run for periods at reduced speed.What are the benefits to a VFD besides speed control ?
You can fix that now. If your VFD has an adjustable carrier frequency (most new ones do now) the audible whine will move out of the range of human hearing at around 8-10kHz (depending on how young the listener is). The VFD's efficiency will drop a little because of the higher switching losses in the transistors, but not much on most modern drives now.Older and cheaper designs sometimes require a slight de-rating of the drive because of this however, so check your manual to see if this may be an issue.Makes the motor emit an audible, annoying whine between 2KHz to 4KHz which is right in the middle of the most sensitive portion of human hearing. This whine seems to be worse the slower you run the motor (or perhaps the noise emitted by everything else is lower so it is easier to hear). I have gotten flack over this in conveyor applications. If wonder if motor manufacturers are considering changing how they make windings in order to reduce this?
The biggest down side of a VFD if you are not concerned about speed control is that the VFD is not 100% efficient. Even the best will present a 2-3% loss of circuit throughput energy in the form of heat in the drive. If you add filters with inductors (reactors), you will increase those heat losses in the circuit. Most of the time if the VFD is running at reduced speed, the losses are proportionally reduced and you are most likely saving some energy anyway. The problem with losses only is a significant concern if you are spending all of your time at full speed and compare that to running across the line, where there are virtually no circuit losses.will a noise filter control the harmonics? would yo use a line reactor with a drive that has a noise filter?
what are the benefits to a vfd besides speed control ?
For many installations the cost of a VFD is comparable to a soft starter alone. But you get the soft starts plus speed control, if needed.
And mine is selling selling variable speed drives.On the other hand, my job is solving harmonics problems, so please use VFDs as much as possible
I'm sure you understand.
Ah, note the smiley at the end of my post.And I thought that engineering companies should sell what is best for the customer.