60A non-fused disconnect downstream of 100A Breaker allowed?

Status
Not open for further replies.

Engineer1

Member
Is there anything wrong with this design scenario?

30 hp, 480V, 3 ph motor fed from a 100A circuit breaker with a 60A local non-fused disconnect. Wire size is #6 & #8G.

Thanks
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

A 60 amp disconnect would be fine in the scenario that you have.

430.110 requires the disconnecting means for a motor to be rated at least 115% of the motor full load current rating.

The full load current rating of a 30 HP 460 volt 3 phase motor in accordance with Table 430.250 is 40 amps, so the disconnecting means must be rated at least 46 amps.

Do make sure that the disconnect has an SCCR at least as high as the available fault current at the motor.

Chris
 

mcclary's electrical

Senior Member
Location
VA
Is there anything wrong with this design scenario?

30 hp, 480V, 3 ph motor fed from a 100A circuit breaker with a 60A local non-fused disconnect. Wire size is #6 & #8G.

Thanks



430.150 has that motor at 40 amps

40x1.15= 46,,,,,so a 60 amp disco meets the requirement 0f 430.110 and the 6's assuming they are copper are ok.




EDIT :sorry chris,,,you're too fast
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Is there anything wrong with this design scenario?

30 hp, 480V, 3 ph motor fed from a 100A circuit breaker with a 60A local non-fused disconnect. Wire size is #6 & #8G.

Thanks
Can we assume there is a motor starter (with overloads) in there somewhere? You aren't planning on using the disconnect to turn the motor on and off are you?
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
HP rated

HP rated

I think the switch must be also be HP rated for the motor it's serving, which if it were a Sqaure D Heavy Duty 60 amp switch it would just meet the 30 HP limit..
JM
 
Last edited:

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Siemens 60 amp fused disco's are rated for 30HP I believe. Their knife switches are 40HP? or so. I know I used a 60 amp knife switch as a local disconnect on a 40HP pump but had to use a 100 amp fused disconect to feed it.
 