Upsizing an existing 500kVA transformer to a 750 in an existing building, the available fault current has obvioulsy increased. The main switchboard is being reconditioned with new breakers. According to my calculations the available fault current at the panelbaords in the tenant spaces is approx 22K. The existing main breaker in the panelboards is GE TQD and branch breakers are THQB, both rated 10K. Any suggestions on what I can do to avoid replacing these breakers in the tenat panelboards. Would it be best to replace all the circuit breakers in the main switchboard with new GE breakers that are series rated with TQD and THQB branch breakers, the contractor prefers to use Cutler Hammer breakers.