What are the issues for a storage type water heater more than 120 gallons? I'm being asked about a 150 gallon WH. Interestingly, most of the commercial grade water heaters only go up to 119 gallons.
Here is all I have found:
422.13: For WH less than 120 gallons, shall be considered continuous load for sizing branch circuit. So if the the tank is 121 gallons, it is not considered a continuous load? That doesn't seem like a good idea.
422.11.F.1: Limited to 48A circuits unless covered by F.3
422.11.F.3: If the unit is an asme rated and stamped tank, then can have heating element circuits up to 120A.
Is this a Mechanical Code issue? Above 120 gallons the vessel must be ASME rated? That would make sense. An ASME rating would really jack up the cost.
Anybody got any clues?
cf
Here is all I have found:
422.13: For WH less than 120 gallons, shall be considered continuous load for sizing branch circuit. So if the the tank is 121 gallons, it is not considered a continuous load? That doesn't seem like a good idea.
422.11.F.1: Limited to 48A circuits unless covered by F.3
422.11.F.3: If the unit is an asme rated and stamped tank, then can have heating element circuits up to 120A.
Is this a Mechanical Code issue? Above 120 gallons the vessel must be ASME rated? That would make sense. An ASME rating would really jack up the cost.
Anybody got any clues?
cf