stew

Senior Member
Can anyone tell me when the rquirement that conductors in a patient care area not be nm? Also when did the code begin not allowing nm above a drop ceiling? This building was constructed in 1984 and has both conditions stated.
 

Volta

Senior Member
Location
Columbus, Ohio
Article 517 was named 'Health Care Facilities' in 1971, and basically took the form it is in today. Before that, it was called 'Flammable Anesthetics', and very short.

1971 517.51(b)(3) "A separate, insulated, continuous, stranded, copper grounding conductor, not smaller than No. 12 AWG, shall be installed with the circuit conductors in the approved wiring system which connects each patient receptacle including the receptacle grounding terminal to the same patient reference grounding bus. . ."

Close, but may not be what you need.
1975 517-51(b)(1) "Each patient bed location shall be provided with a minimum of four single or two duplex receptacles, each receptacle shall be grounded by means of an insulated copper conductor sized in accordance with Table 250-95. . ."

Tha would prohibit almost all NM, but NM and NMC were permitted to contain an insulated grounding conductor that year 336-2.

NM was specifically allowed by exception No. 2 to Section 517-11(a) to have the EGC be uninsulated in Clinics, Dental Offices, Outpatient Facilities, Nursing Homes, and Residential Custodial Care Facilities in 1981.

You would have to be subject to the 1990 or newer cycle to find that exception disappear.

So 1990 is when it was not allowed at all in any Patient Care Area.
 

eprice

Senior Member
Location
Utah
sounds like that in 1984 both situations i have listed were ok at that time and should still be allowed today as is.

Well, does the NM used have an insulated equipment grounding conductor? If not, it cannot be used in the patient care areas.

oops.. missed that exception #2
 
Last edited:

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
The requirement for patient care areas has not changed which in 1984 was in part B, "....shall be grounded by an insulated copper conductor..."

Exception No.2 said: An equipment grounding conductor enclosed in the sheath of a nonmetallic-sheathed cable assembly installed in accordance with the limitations of sections 336-3 and 336-4 shall be permitted to be used in accordance with parts C and D of this article.

Part C was Clinics, medical, and dental office, outpatient facilities and other health care facilities not covered in parts D and E

Part D was nursing homes and residential custodial care facilities

Part E was hospitals

If you read the wording in 517-11 and then read the wording in 517-30 they seem to conflict.

In 1990, the code talks about the type of conduit you have to use In 517-13(a) and (b) and the exception from NMC has been taken out.
 