I am wanting to install a 150kVA, 4160D:208Y/120, Al, dry-type transformer in a building. Code says I need Class 155 Insulation unless I enclose it in a 1 hour fire rated room. Is this custom or do transformer manufactures typically make this insulation class as a standard offering?
The transformer manufacture I was looking at (Hammond) apparently has Class 220 as a standard offering which I am assuming is worse than Class 155. Although the code says "or higher", but I figure the code is referring to a insulation which will not get hotter than Class 155 ...
Also, it says in Exception #2: "completely enclosed". I am also assuming that a NEMA 3R enclosure would satisfy this requirement, yes?
I always enjoy it when people post the code section they are referring to:
NEC 2008 450.21(B):
(B) Over 1121⁄2 kVA. Individual dry-type transformers of
more than 1121⁄2 kVA rating shall be installed in a transformer
room of fire-resistant construction. Unless specified
otherwise in this article, the term fire resistant means a
construction having a minimum fire rating of 1 hour.
Exception No. 1: Transformers with Class 155 or higher
insulation systems and separated from combustible material
by a fire-resistant, heat-insulating barrier or by not less
than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically.
Exception No. 2: Transformers with Class 155 or higher
insulation systems and completely enclosed except for ventilating
openings.
The transformer manufacture I was looking at (Hammond) apparently has Class 220 as a standard offering which I am assuming is worse than Class 155. Although the code says "or higher", but I figure the code is referring to a insulation which will not get hotter than Class 155 ...
Also, it says in Exception #2: "completely enclosed". I am also assuming that a NEMA 3R enclosure would satisfy this requirement, yes?
I always enjoy it when people post the code section they are referring to:
NEC 2008 450.21(B):
(B) Over 1121⁄2 kVA. Individual dry-type transformers of
more than 1121⁄2 kVA rating shall be installed in a transformer
room of fire-resistant construction. Unless specified
otherwise in this article, the term fire resistant means a
construction having a minimum fire rating of 1 hour.
Exception No. 1: Transformers with Class 155 or higher
insulation systems and separated from combustible material
by a fire-resistant, heat-insulating barrier or by not less
than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically.
Exception No. 2: Transformers with Class 155 or higher
insulation systems and completely enclosed except for ventilating
openings.