ceb58
Senior Member
- Location
- Raeford, NC
Situation. 45kw gen. set non-SDS 1ph 240v at communication tower. Contractor that installed the gen. and transfer switch bonded the neutral and ground at the gen. disconnect which I know is wrong and will be changed PDQ. But what has me wondering is they did not pull an EGC with the feeders from the gen set to the disco they instead bonded the frame off of the underground grounding ring with a #2 solid. There are 2 places on the gen. to install an EGC. One is on the frame and the other is on the sheet metal enclosure where the breaker on the gen. is located. Mechanically they are together through the gen. frame. Should another EGC be pulled with the feeders and be bonded in the enclosure? We have had some lightning strikes at this site and every time something in the transfer switch and/or the gen. gets fried. I think the main reason is due to the fact they did not separate the N-G in the gen. disconnect.