This question to the folk working on hospital facility and design (NEC 517 and NFPA-99 related rule):
Will manual transfer switch be allowed to serve emergency - equipment power branch system? Thanks!
517.31 Emergency System
Those functions of patient care depending on lighting or appliances that are connected to the emergency system shall be divided into two mandatory branches: the life safety branch and the critical branch, described in 517.32 and 517.33.
The branches of the emergency system shall be installed and connected to the alternate power source so that all functions specified herein for the emergency system shall be automatically restored to operation within 10 seconds after interruption of the normal source. [NFPA 99:4.4.2.2.2.1, 4.4.3.1]