The NEC does not cover automotive applications. Are you talking about something at your home, or is this somehow job related?
 

amoss38

Member
Location
Michigan
Number of wires under a grounding terminal

Number of wires under a grounding terminal

Electrical control panels for various types of manufacuring machine
 

amoss38

Member
Location
Michigan
More than one wire under a terminal.

More than one wire under a terminal.

It's a distribution block with more than one wire under a terminal. I thought it may have something with losing my ground continuity.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
It's a distribution block with more than one wire under a terminal. I thought it may have something with losing my ground continuity.

The distribution block must be indentified for more than 1 conductor under a lug for the application.

As already mentioned take a look at 110.14(A).