Reliability Issues

Status
Not open for further replies.

Jed057

New member
Hi,

there have been frequent trips in our factory, we will have a meeting with our electrical specialists involved in reliability.

What topic we should review to improve reliability ?


young engineer
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
100422-0844 EST

Put some monitoring equipment on the circuits to see what type of signal occurs and timing. Monitor voltage and current of each phase, and neutral, and maybe the EGC.

The design of your system will really define what you need to monitor. I would suggest you want 1 second sampling plus some instantaneous information. The 1 second sample rate will produce large files of data.

You can not reasonably store relatively instantaneous data for very long and therefore this monitoring should have some thresholding limits to control when data is saved.

.
 

zog

Senior Member
Location
Charlotte, NC
Hi,

there have been frequent trips in our factory, we will have a meeting with our electrical specialists involved in reliability.

What topic we should review to improve reliability ?


young engineer

When is the last time a coordination study was performed? That should be the first thing you look at.

When is the last time your breakers were tested? A common failure of breakers with electronic trip units is for them to fail to the defaults, which is usually the minimum settings.
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
would check the trip settings on your service breakers. Also, monitor the amperage on the GEC.. Worked in a plant one time that had 8 amps flowing on the grounding system that caused the mains to trip occasionally.. .
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Could you further explain this scenario?

Sure..... Someone at the plant wired a panel the wrong way.. Caused a

ground loop in the system which resulted in 8 amps flowing on the GEC. When

you put an amp clamp on the green wire, it read 8 amps... The miss-wiring

caused just enough current to be shunted to Ground that the GFCi protected

Main breaker would occasionally trip..
 

dbchamblee

Member
Check for harmonics, particularly on the circuits that have tripped. High levels of harmonic current can cause false trips.
 