Bunn dual with faucet was donated to a local church. Name plate states 120/208 1 phase 3 wire 28.7A. It wont be a continuos load so 30A breaker is ok correct? What NEMA config would you guys recommend? It didn't come with the cord.
 

iwire

Moderator
Staff member
Location
Massachusetts
I have never seen a coffee maker that would meet the definition of continuous load. If the burners had no thermostats they would boil the coffee while it sits there.
 

iwire

Moderator
Staff member
Location
Massachusetts
I would use a 30 amp circuit with a 30 amp plug and receptacle.

I suggest a look at the Article 100 definition of continuous load. It is not enough that the switch is on for more than 3 hours the maximum load must be applied for more then 3 hours before we have to call it a continuous load.

If you do decide to go to a 40 you will be into a 3 wire range receptacle and cord.:)
 
Since the name plate states 120/208 wont it have a neutral on it? Thus requiring a four wire plug? I apologize guys, it has been 2 years since i had to figure any of this out and I know the confusion on my part seems a bit simple minded. The plate say 120/208 3 wire. Bahhhh!!!!!!
 

iwire

Moderator
Staff member
Location
Massachusetts
Since the name plate states 120/208 wont it have a neutral on it? Thus requiring a four wire plug? I apologize guys, it has been 2 years since i had to figure any of this out and I know the confusion on my part seems a bit simple minded. The plate say 120/208 3 wire. Bahhhh!!!!!!


You are right, I did overlook the 120 volt part.
 

Hameedulla-Ekhlas

Senior Member
Location
AFG
Bunn dual with faucet was donated to a local church. Name plate states 120/208 1 phase 3 wire 28.7A. It wont be a continuos load so 30A breaker is ok correct? What NEMA config would you guys recommend? It didn't come with the cord.

I suggest you to go with 30 ampere:

and for more information click here
 
Last edited:

jumper

Senior Member
Since the name plate states 120/208 wont it have a neutral on it? Thus requiring a four wire plug? I apologize guys, it has been 2 years since i had to figure any of this out and I know the confusion on my part seems a bit simple minded. The plate say 120/208 3 wire. Bahhhh!!!!!!

Here is a link to Bunn coffee makers

http://www.bunnomatic.com/pdfs/commercial/specsheets/a27.pdf

note the electrical

Electrical: Brewer is 3-wires plus ground service rated 120/208V or 120/240V, single phase, 60Hz.
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
I suggest a look at the Article 100 definition of continuous load. It is not enough that the switch is on for more than 3 hours the maximum load must be applied for more then 3 hours before we have to call it a continuous load.

:)

I've often wondered how the CMP's justified calling a storage type water heater a continuous load in light of your observation, Bob.
 