I am relatively new to electrical contracting and I am doing my first residential basement finishing project installing a 100A sub panel to feed the load. I am wanting to install SE wire from the main to the sub panel. I have looked in 338.10 for installation requirements. In 338.10(A)(4)(a) it points me back to part II of 334.

My total load is only 51A. My questions are:

1) Is #4 SE cable overkill for this installation? It is 70' of wire and voltage drop looks good.
2) 334.10 seems to say I do not have to install it in conduit. Is that correct?

I appreciate any responses because I just want to make sure I get this to code with no issues.

Varczar

If you are installing a 100 amp sub panel, I do not care what you are tying into it right now... I really suspect that the inspector will say it has to have the capacity to carry a total load of 100 amps... so that's either #4 copper, or #2 aluminum SER. SE has three wires... SER has 4... anytime you install a sub panel, the ground must be connected to the box and the neutral must be isolated from the ground. Remember to add a separate ground bar if the box doesn't have a second one built in. and remove the ground tab from the neutral bar (if it comes built in).
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you are installing a 100 amp sub panel, I do not care what you are tying into it right now... I really suspect that the inspector will say it has to have the capacity to carry a total load of 100 amps...

may be true in your area, but not here. The load would determine the feeder size. I see a lot of 100 amp panels with 60 amp feeders. If you or the customer want load diversification, almost any panel over 8 or 12 circuits will be bigger than 60 amps.
so that's either #4 copper, or #2 aluminum SER.
under the '08 Code, SE (SER) would only be #4 SE would be 70 amps and #2 SE AL would be 75. Neither would be 100.
SE has three wires... SER has 4... anytime you install a sub panel, the ground must be connected to the box and the neutral must be isolated from the ground. Remember to add a separate ground bar if the box doesn't have a second one built in. and remove the ground tab from the neutral bar (if it comes built in).
 