This is probably more an NFPA quesiton then NEC but I can't find a NFPA forum with members that I like as much as you guys.
I have an application where the building is constructed of an in floor raceway system so I can't screw into the ceiling deck because it's a raceway for the floor above. I need to install smoke and heat detectors in the elevator equipment room, the only way I can attach to the ceiling deck will result in the fire alarm device being installed about 4 1/2" below the ceiling deck. Do any of you know if it is stated somewhere that a detection device can only be suspended below a flat ceiling a certain amount? I know if mounted on a sidewall it must be a minimum of 4" and a maximum of 12" of from the ceiling. Any insights on this issue or recommendations for a good NFPA 72 forum?
I have an application where the building is constructed of an in floor raceway system so I can't screw into the ceiling deck because it's a raceway for the floor above. I need to install smoke and heat detectors in the elevator equipment room, the only way I can attach to the ceiling deck will result in the fire alarm device being installed about 4 1/2" below the ceiling deck. Do any of you know if it is stated somewhere that a detection device can only be suspended below a flat ceiling a certain amount? I know if mounted on a sidewall it must be a minimum of 4" and a maximum of 12" of from the ceiling. Any insights on this issue or recommendations for a good NFPA 72 forum?