Dedicated Circuits
augie47
Tennessee
yes, yes, yes, if the circuit is a 15 amp circuit. :grin: Art. 210.52(B)(1)except. 2
Dennis, I don't know if that requires it to he dedicated. Can I not still feed my pantry light (etc) from that circuit ?
{as long as I comply with 210.23(A)(1)}
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I don't think so. It reads clearly to me if you use a 15 amp circuit then it must be from an individual branch circuit.
Anyone else have input.
augie47
Tennessee
I enjoy your posts. :)
I had not given that thought.... in NEC language is "individual circuit" a "dedicated circuit"... quite possible ...
as you ask.. others ????
mcclary's electrical
VA
Although I agree with Dennis, I cannot produce solid definitions of dedicated branch circuit vs individual branch circuit
charlie b
Lockport, IL
Retired Electrical Engineer
Ah, but riddle me this: I have a refrigerator that is plugged into a receptacle on a 20 amp branch circuit that also powers the nearby overhead light, and this is not an NEC violation! How? :-?
My understanding was that any fixed appliance in a kitchen should have a dedicated circuit. Refers, garbage disposals, dishwashers are always on there own circut..... at least in the homes I rope.
charlie b
Lockport, IL
Your understanding is incorrect.
Depends on the meaning of the word, "should." ;) Is it required by code? No. Is it a good design and installation practice? Yes. Is it worth the additional cost? That is up to the owner.
augie47
Tennessee
Dennis, you are correct and I as wrong.
I looked for but missed the NEC definition of "Branch Circuit, Individual".
Refrigerators on a 15 amp circuit must have no other utilization equipment.
Does the NEC require refrigerators to be on a dedicated circuit?
Not required.
Applies only to dwelling kitchens and basically permits it to not be on small appliance branch circuit. If you put it on 20 amp circuit it is a small appliance branch circuit even if only receptacle on the circuit - and you could have only one other SABC installed and still meet code.
