Can someone explain this with some examples...:-?
Thanks
This is very common, and normal in the power industry whereby you utilize the HV substation or switch-yard for power needed to start the auxiliary power system loads, in order to start the generating unit; done when the generator is connected to the system through a generator breaker and there is not a separate station service transformer.
It is accomplished by keeping the generator breaker closed, and feeding power to the auxiliary power system through the step-up transformer, (in this case step down) and then through the auxiliary power transformers to the loads. When the unit is up and running at synchronous speed, you can close the generator breaker upon synchronization with the system, thereby the generator now provides power simultaneously to the loads, and the excess to the system.