Trip rating and withstand rating are two different things.
For instance the breaker may be capable of withstanding 14,000 amps, but it may be set to trip at 5000A. So as long as the fault current is limited to 14,000 A or less, then it will not be damaged. However, if you set it at 5000 A to trip instantaneously (magnetic) and there is only 4000A of fault current, the breaker will not trip for the fault.
Very important to do fault current calculations and protective device coordination.