This doesn't sound like a 6 lead motor, it sound like a 9 lead motor. Typically a dual-voltage, 6 lead motor is connected as delta for low voltage and as wye for high voltage. That is, for low voltage you'd connect 1&6, 2&4 and 3&5 and for hi voltage you'd connect 1, 2, 3 and tie 4-5-6 together. However, this type of motor would provide a 1.732 ratio from hi-to-low voltage. You indicate a 2:1 voltage ratio.
A nine lead motor typically has the same 6 leads as above, but has another three leads from another set of winding that has an internal wye connection. For low voltage you'd connect 1&7, 2&8, 3&9 and tie 4-5-6 together. This would connect the two sets of winding in parallel in a wye configuration.
For high voltage, the 9 lead motor is connected as 1, 2, 3 and you join 4&7, 5&8, 6&9. This connects the two sets of windings in a series connection in a wye configuration. The 9 lead dual voltage motor has a 2:1 voltage ratio. It would appear from your description: a 2:1 ratio, connecting 1&7, etc, that you have a 9 lead motor.