If any of the remaining loads are connected line-to-neutral, there will be neutral current, which is what keeps the load end maintained at (or near) the supply neutral's voltage, which is hopefully real close to zero.
If you have a balanced MWBC, and switch off one phase's load, the neutral current will become what the removed current was. For each amp you remove from a phase, the neutral current increases by that same amount
Why if the 3 phase wye load with a connected source neutral lost a phase would there be current on the neutral? Why wouldn't the current just be L-L on the two remaining phases?
So if I did have a 3 phase wye load that had a neutral connected, and all phases were balanced, then why would there be no current on the neutral in this case? Why would all currents be balanced on the other phases when the impedance to the neutral is less? Is there an equation involving phase angles that shows this?
My OP is simply a theoretical question to help me understand, but in reality if I had a 3 phase load (heater etc..) that the OEM shows as having a neutral connected but I only have a 3-wire system, then can I still go aheand and connect this load without a neutral? Obviously if all phases are balanced then there will be no issue, but would the issue of unbalance be a problem if neutral point of the load rose above zero volts?