I was checking some of the power meters on some of our 4.16kV feeder breakers the other day when I noticed a particular feeder circuit having a somewhat high Total Harmonic Distortion (THD) on one of the phase currents. The %THD on the phase currents were:
Ia = 5.5%
Ib = 13.5%
Ic = 4.3%
I know the IEEE standard (I believe standard 519) states that the maximum %THD for current should be 5%. Seeing that I have slightly over 5% on Ia and almost 3x that on Ib, do you think this warrants a cause for concern and additional investigation? I also set the meter up to record max values and at some points it shows %THD on current as being as high as 181%.
The 4.16-480V delta-wye transformer that this feeder feeds seems somewhat louder than the remaining similar transformers that we have. Could this be a result of this high harmonic content on phase Ib?
There are no VFD's on the secondary of this transformer, and the only non-linear loads are really just lighting. I briefly looked at the harmonic spectrum and most of the distortion seemed to be from the 5th harmonic which would indicate a 6-pulse drive on the system. Any ideas what else could be causing harmonics?
On the same lineup as this feeder breaker there is a main breaker who's meter only shows 2-3% THD on the phase currents. Is this value less here, b/c the % distorted current on the feeder breaker is a much smaller portion of the toal current on the main breaker? In other words is THD the acutal % of the total current so for a smaller current on a feeder breaker it may be large but when mixed with the toal current on a main breaker it may become smaller?
Ia = 5.5%
Ib = 13.5%
Ic = 4.3%
I know the IEEE standard (I believe standard 519) states that the maximum %THD for current should be 5%. Seeing that I have slightly over 5% on Ia and almost 3x that on Ib, do you think this warrants a cause for concern and additional investigation? I also set the meter up to record max values and at some points it shows %THD on current as being as high as 181%.
The 4.16-480V delta-wye transformer that this feeder feeds seems somewhat louder than the remaining similar transformers that we have. Could this be a result of this high harmonic content on phase Ib?
There are no VFD's on the secondary of this transformer, and the only non-linear loads are really just lighting. I briefly looked at the harmonic spectrum and most of the distortion seemed to be from the 5th harmonic which would indicate a 6-pulse drive on the system. Any ideas what else could be causing harmonics?
On the same lineup as this feeder breaker there is a main breaker who's meter only shows 2-3% THD on the phase currents. Is this value less here, b/c the % distorted current on the feeder breaker is a much smaller portion of the toal current on the main breaker? In other words is THD the acutal % of the total current so for a smaller current on a feeder breaker it may be large but when mixed with the toal current on a main breaker it may become smaller?