mark32
Senior Member
- Location
- Currently in NJ
I had the opportunity to work with some friends the other day that needed to finish a house asap. When the breakers were turned on, one 15a dp afci (Siemens) would trip as soon as any light on one of the circuits was turned on. After checking numerous splices we came to the great room that had six high hats, three on the sloped part of the ceiling and three on the flat, 18' high. All of the splices looked good, of course, I then suggested doing a continuity check between the neutral and ground of the cables between the lights. With the splice apart at the first high hat, on the flat, we had continuity from the ground to neutral down to the sloped high hat. My one buddy then took that splice apart and the continuity went away. Huh? He then grabbed the tester and said that the socket was bad. What had happened was this, on the bracket that the socket mounts to is a little tit that is suppose to keep the socket from spinning when a bulb is installed. (There is an indentation on the socket for this tit) The problem is that this tit was making contact with the same part of the socket that the grounded conductor terminates to. Luckily there is another indentation on the socket so he was able to spin the socket for that indentation to line up with the tit. This had to be done on all three Halo H745ICAT's! One this repair was done the breaker held. Just a heads up if you run into a similar problem. One question that remains, why would the circuit trip when any of the other lights on that circuit were turned on??