Step Down Transformer

Status
Not open for further replies.

Ed Kelley

New member
Recently I had a Inspector classify a 5Kv transformer as a "Separately Derived System" Was on a 480V Y systerm step down to 240/120V Single phase. to power a 6cir panel for a battrey charger and a area light and 1 GFCI. He had me run a # 6 ground Back to the main system Ground rod , Making a Parallel ground. and MAde me run the Secondary in # 6 THHN to the panel.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The inspector was correct in his calling that a SDS.
Since you were powering 120 devices, you obviously needed a neutral.
A SDS must have a GEC to an electrode as defined in 250.30. You would need to review 250.30(A)(7) to see if the rod was the appropriate GE.
 

DARUSA

Senior Member
Location
New York City
The inspector was correct in his calling that a SDS.
Since you were powering 120 devices, you obviously needed a neutral.
A SDS must have a GEC to an electrode as defined in 250.30. You would need to review 250.30(A)(7) to see if the rod was the appropriate GE.

If he doesn't use a 120volt loads it make a diferent in
the classification of SDS?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It would still be a SDS by definition.
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.
and
250.20(B) would require the neutral bond whether used or not, IMHO

(B) Alternating-Current Systems of 50 Volts to 1000 Volts. Alternating-current systems of 50 volts to 1000 volts that supply premises wiring and premises wiring systems shall be grounded under any of the following conditions:
(1) Where the system can be grounded so that the maximum voltage to ground on the ungrounded conductors does not exceed 150 volts ...............................
 

raider1

Senior Member
Staff member
Location
Logan, Utah
It would still be a SDS by definition.
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.
and
250.20(B) would require the neutral bond whether used or not, IMHO

(B) Alternating-Current Systems of 50 Volts to 1000 Volts. Alternating-current systems of 50 volts to 1000 volts that supply premises wiring and premises wiring systems shall be grounded under any of the following conditions:
(1) Where the system can be grounded so that the maximum voltage to ground on the ungrounded conductors does not exceed 150 volts ...............................

I agree with Gus.:)

Chris
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Ed, welcome to the forum! :)

In a nutshell, the secondary of a transformer is the origination of a new suppply source, so it needs a grounding electrode system, as well as having the new neutral bonded to that system.
 