What is the difference between emergency lights and egress lights?
I believe emergency lights are often considered egress lights based on the wording in the buildg code.
IBC 2006
1006.1 Illumination required. "The means of egress, including the exit discharge, shall be illuminated at
all times the building space served by the means of egress is
occupied."
Exceptions:
1. Occupancies in Group U. (Utility)
2. Aisle accessways in Group A. (Assembly)
3. Dwelling units and sleeping units in Groups R-1, R-2, and R-3(Motels, Apartments, and Single-family)
4. Sleeping units of Group I occupancies. (Institutional)
1006.3 Illumination emergency power. "The power supply for means of egress illumination shall normally be provided by the premises' electrical supply."
"In the event of power failure, an emergency electrical system shall automatically illuminate the following areas: ............."
Since the means of egress must be lit at all times when the building is occupied, if power fails to the normal lighting, the emergency lights become the egress lighting. IMO