120/240 V, 3 phase NOT Delta CT????

Status
Not open for further replies.

master1

Member
We are designing a machine for a customer who said they have:

240 vac / 120 vac

We need 3 phase for our machine.

I want to be sure they did not mean 208/120 wye so I went over to the plant.

3 Pole main / Nuetral bus / ground bus in panel OK

2nd pole had org tap OK probably center tap of delta but know high leg (208v)

239 V A-B
239 V B-C
239 V A-C

120 VAC A-N
120 VAC B-N
120 VAC C-N

Does anyone have experience with this type of system.

I left thinking we should be fine (not sure of how they were doing this) had 3 phases and 120 vac. I just had my Fluke meter and did not verify this was a true 3 phase system???

First post Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome to the Forum.

Most unusual (to me). Did you measure from the line side lugs ?
Some 240/120 hi-leg panels have a breaker arrangement where Phase B drops out after the 1st few breakers so if you measured off load breakers B phase may not have been present..
With 120 to ground on all three one would think 208Y-120 but obviously the 239 is high especially in relation to the 120.
Can you request info from POCO ?
 

master1

Member
Revising post

Revising post

Just read my post

1. know means no
2. want means wanted
3.
These are the voltages a read with my fluke
239 V A-B
239 V B-C
239 V A-C

120 VAC A-N
120 VAC B-N
120 VAC C-N
 

master1

Member
Most unusual (to me). Did you measure from the line side lugs ?

Yes, great point

I do not remember seeing any three phase breaker other than the main

I should have check the number of bus bars

Some 240/120 hi-leg panels have a breaker arrangement where Phase B drops out after the 1st few breakers so if you measured off load breakers B phase may not have been present..


With 120 to ground on all three one would think 208Y-120 but obviously the 239 is high especially in relation to the 120.

Yes and the 120 was 120 not higher?

Can you request info from POCO ?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Your readings do not follow the laws of physics for a solidly grounded system.

A system where all three phase voltages have the same voltage to neutral, means you must have a wye connection from the utility. The L-L and L-N voltages in a wye system must be different by the square root of 3 (~1.732) yielding either 208Y/120 or 240Y/136 as the nominal voltages.

In a center tapped delta system one L-N voltage must be 1.732 times the other two L-N voltages.

Did you measure the N-G voltage?
Did you measure the L-G voltages?
 

master1

Member
Moderator,

Just started digging into this problem.

Is the reason they drop the b phase (have no B bus at all in panel even though 3 phase breaker) to be sure that the panel does not have the high leg voltage available?

This way a electrician (or ignorant engineer) would not have the ability to wire (and outlet / branch circuit) into the high leg bus (obvious now / I think)

Thanks
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I would say the panel was not three phase, but single phase, I have done this before using a three phase main disconnect feeding a wireway tapping off for a single phase panel for general power, then tapping off with three phase disconnects for the few three phase loads that they had.
 

master1

Member
Jim,

I measured (from the main supply lug / not load side):

239 V A term - B term
239 V B term - C term
239 V A term -C term

120 VAC A-N bus (white / many neutral wire connected) right side of panel
120 VAC B-N
120 VAC C-N

Green - ground bus was on the left side of the panel many green wires connected.

I should have but did not check the voltage between ground bar and neutral bar. Also did not check for bonding between the two.

It was a clean (well wired / prof. job) panel in an industrial plant

I am about ready to go back and look at the transformer if I can find it

I am with you on the calculations / that is why I am looking for answers
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Is the reason they drop the b phase (have no B bus at all in panel even though 3 phase breaker) to be sure that the panel does not have the high leg voltage available?

This way a electrician (or ignorant engineer) would not have the ability to wire (and outlet / branch circuit) into the high leg bus (obvious now / I think)

Yes it is.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I should have but did not check the voltage between ground bar and neutral bar. Also did not check for bonding between the two.
A lack of appropiate neutral-ground bonding and/or an open neutral can create all sorts of wierd voltage readings.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Is it possible that this was an ungrounded 240V delta system that had a grounded neutral point created by a zig-zag transformer or other method?

I've never seen a zig-zag transformer installation, and haven't been able to find any good information on what the "created" line-to-neutral voltage would be.

Maybe someone here is familiar with them.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Is it possible that this was an ungrounded 240V delta system that had a grounded neutral point created by a zig-zag transformer or other method?
A zig-zag effectively creates a wye transformer, therefore the L-N voltage is Vll/1.732 = 240/1.732 = 138V.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
A zig-zag effectively creates a wye transformer, therefore the L-N voltage is Vll/1.732 = 240/1.732 = 138V.

I guess that's true. I got thinking about it after reading that the windings of the zig-zag transformer should be "rated" for 1/3 of the system voltage, and wondered what would happen if the rating was more or less than 1/3. But after looking at a zig-zag connection diagram, you can see that there will be a voltage drop across each winding of 1/3 the system voltage, regardless of what the winding is "rated for."
 