Look at 250.52(A)(3). This means that the CEE never has to be larger than #4 copper no matter what size service you have. You can use a larger conductor but it is not required.a #4 rebar for concrete encased electrode is good for up to how many amps
Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located horizontally near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
It is supposed to be tied to the rebar if there is 20' of 1/2" rebar in the footingWhen installing a bare Cu. wire for use as a Ufer Ground, can the Cu. wire touch or be tied to the rebar in the footing?
When installing a bare Cu. wire for use as a Ufer Ground, can the Cu. wire touch or be tied to the rebar in the footing?
Yes, the copper can touch the steel in the footing and foundation.
Chris
???????-- it is required by code to tie to the rebar. :-? I assume that is not an issue since we attach copper to galvinized rods all the time.Galvanic reaction?
Dennis I am not sure if we are required to connect to the steel if we have 20' of 4 AWG in the cement but that said I have seen it argued both ways with no clear cut answer.
I read it as an either/or. No attachment required if you have the 20' of bare copper.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system.
Dennis I am not sure if we are required to connect to the steel if we have 20' of 4 AWG in the cement but that said I have seen it argued both ways with no clear cut answer.
Is twenty feet of 4 AWG in a concrete footing an electrode?
Is twenty feet of 1/2" re-bar in a concrete footing an electrode?
Now what does 250.50 say?
Just pointing it out ........... :grin:
???????-- it is required by code to tie to the rebar. :-? I assume that is not an issue since we attach copper to galvinized rods all the time.
Galvanic reaction?
One could also argue that the rebar trumps the 20' of #4 simply because the rebar (an electrode) is present and therefore it must be used.