Need a Ground Rod Installed?

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
By the NECs definition of structure, there is no such thing as a detached structure where the NEC is relevant :)

A structure is 'that which is built or constructed'. Wiring is built or constructed. If I construct a building with some wires underground to a pole, I have a single structure, since the building and the pole are continuously connected by a constructed path. :) If I have two separate structures and I run wires between them, I have rendered them a single structure.

-Jon
 

mcclary's electrical

Senior Member
Location
VA
By the NECs definition of structure, there is no such thing as a detached structure where the NEC is relevant :)

A structure is 'that which is built or constructed'. Wiring is built or constructed. If I construct a building with some wires underground to a pole, I have a single structure, since the building and the pole are continuously connected by a constructed path. :) If I have two separate structures and I run wires between them, I have rendered them a single structure.

-Jon



I agree, and touching on what Dennis said, most inspectors around here DO consider the pumping station a seperate structure, so everything he said applies. GES,,,,and feeder instead of two circuits
 

Volta

Senior Member
Location
Columbus, Ohio
By the NECs definition of structure, there is no such thing as a detached structure where the NEC is relevant :)

A structure is 'that which is built or constructed'. Wiring is built or constructed. If I construct a building with some wires underground to a pole, I have a single structure, since the building and the pole are continuously connected by a constructed path. :) If I have two separate structures and I run wires between them, I have rendered them a single structure.

-Jon

Wow- what a thought. It's all one building. Cool!
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Because while I think winnie's 'no separate structure theory' is interesting I have no doubt the CMPs will not agree with it.

Amen.

I think that we would all agree that there really are 'detached structures', and we probably agree on the majority of cases. We'd probably find a few grey area cases that would lead to 600 post threads, and we'd probably find a quite a few things that most of us would agree are 'detached structures' but we'd question if the same rules should apply.

I believe that as worded the current definition of detached structure neither agrees with nor clarifies the common understanding of the term.

-Jon
 

One-eyed Jack

Senior Member
I tend to agree with the structure concept but that in itself creates other issues.

Let's look at a septic pump setup. Many of these units require 240v for the pump and 120v for the alarm. In some systems the alarm is tied to one leg of the pump-- problem-- yes. Since the 2008 we now have to have a dp breaker installed which would trip out the alarm on a short circuit or ground fault on the pump. Damn the alarm won't work. This makes this install illegal, at least around here.

Now run two circuits - a 240v circuit for the pump and a 120v circuit for the alarm. Problem again-- 225.30 unless one of the special conditions would apply (I didn't think it would). So if it's a structure, which I say yes to, then there is no legitimate way to wire the septic pump system.

I believe there must be an answer somewhere but as the NEC is written there isn't much that wouldn't qualify as a structure if it is detached from the building serving it. What is the intent-- who knows.

If it is UL listed and the mfg. instructions require two circuits,which all I have seen do I don't have a problem with it, be it a double pole and a single or two single pole breakers.

True.The definition of structure could use a little more thought.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If it is UL listed and the mfg. instructions require two circuits,which all I have seen do I don't have a problem with it, be it a double pole and a single or two single pole breakers.

True.The definition of structure could use a little more thought.

I find that most inspectors overlook this and allow 2 circuits. In orange county, nc they made the manufacturer change the setup of the box so that it could accept 2 circuits. They did not want the breaker to trip and have no alarm. The mfg. complied.
 

radiopet

Senior Member
Location
Spotsylvania, VA
We are going to install a new outdoor MLO subpanel to a conrete pole. It will get fed from a 208/120v 3 phase panel. The new panel will have 3 breakers in it serving a camera and lighting. Since it is not in a building or a structure, do we need to install a ground rod for this new subpanel?

Code says it is a structure in itself(that which is built)...so yes you will need to establish a grounding electrode system in accordance with NEC 250.50
 