11Haze29
Member
- Location
- Rhode Island
- Occupation
- Electrical Engineer
Industrial application to install 2500KVA padmount xfrm,480V, 3ph. Under normal condition I would feed 3200amp switchgear with 5 each 800a branch breakers. But customer wants cheap as possible, so I want to ask what you think of this. Article 230.71 permits six switches/breakers for a service. Is it possible to set up five each, 800A fused disconnects in the electric room, then take two each 500MCM copper XHHW feeders from the line side of each FSD back to the transformer lugs. FSD's will be rated for 'Service Entrance'. The FSD lugs would be rated 75C, Size 500MCM in 310.16(75C) is rated 380amps. 240.4(B) permits devices 800A or less to round up the conductor ampacity. So if 500MCM can round up to 400A, in parallel can it be 800Amps.
Will most utilities permit you do this. When I see the six breakers its usually from a main bus. But I can't see why it can't also be done as described above.
Welcome your suggestions.
Will most utilities permit you do this. When I see the six breakers its usually from a main bus. But I can't see why it can't also be done as described above.
Welcome your suggestions.