Seiman's Generator Ready Load Center

Status
Not open for further replies.

mcclary's electrical

Senior Member
Location
VA
I've never been a fan of that type, or any type that allows the owner to overload the generator. I always install a generator fed sub panel and only put the circuits in that panel that I want to run.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I haven't, but you should be able to find info on the www easily enough. You should have a model number by now.
 

techntrek

Member
Location
MD
"Unlike a standard load center, which has only one interior, the generator ready load center has two interiors. During normal operating utility conditions, both interiors are powered. During generator back up conditions, only the lower interior containing critical circuits is powered."

So basically a sub within the service panel. I like.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I just don't like the possibility of them causing their own brownout.
It would be easy to overload a genny even with a genny panel unless you limit the connected loads to the genny's capacity. I want more choices in what I use than that would permit.

I only install a fool proof system.
'fool proof' LOL, i like that. :)
I was gonna say, "Then they come out with a new and improved idiot."


But, I won't. :cool:
 