Is there an NEC, OSHA, or NFPA, rule that forbids taping the rubber cord to the fixture chain of an 8' or 4' fixture (fixture is made with a cord & plug)?
Is there an NEC, OSHA, or NFPA, rule that forbids taping the rubber cord to the fixture chain of an 8' or 4' fixture (fixture is made with a cord & plug)? I forgot to mention we were written up for taping the rubber cord up the fixture chain to the receptacle. I could not find any where in the NEC that saya this is a violation......
Ya how'd knowI've seen it done . Who wrote you up , company safety people ?
Is there an NEC, OSHA, or NFPA, rule that forbids taping the rubber cord to the fixture chain of an 8' or 4' fixture (fixture is made with a cord & plug)?
NEC 400.8 Uses Not Permitted said:Unless. specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
...
(4) Where attached to building structures
...
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
...